Hydro elaborated
Hi Rick
Sorry I didnt put a bit more info with my message, I wasnt sure if you would reply.
So here is a full explanation:
Gross head is 13 meters and by my calculations net would be 11. The pipe through the dam wall is 100m and 300mm is diameter. The size of the turbine intake would allow 160l/s, 2.26m/s water velocity through the 300mm pipe which i used to get friction losses.
The turbine was built by Otago University here in NZ and ive been told that shaft RPM at 10m of head will be 880 at its most efficient speed. It is currently set up to run v belts.
All of the Power generated will need to go directly onto the grid but I have many meters on my bill so I have talked to the power company and the power created will cancel at 1-1 some of the other power I use.
Im still confused as to the possibility of over revving an induction motor that is of a larger rating than our maximum theoretical power available.
The motor I have is 22 Kilowatt, 400 volt, 1400 rpm induction motor. If maximum power is generated at 1442 RPM and I was to rev it up over this under no load then turn it on- would the torque created by the power generation not slow down the motor to below 1442 to an equilibrium point (still above synchronous speed) where the force created by the turbine would equal that by the generation of power by the motor (less losses due to belts, friction etc) eg 10kw.
I had looked into ram pumps but it would not be feasible.
Thank you very much for your time
Kind Regards
Tim
Hi Rick
Sorry I didnt put a bit more info with my message, I wasnt sure if you would reply.
So here is a full explanation:
Gross head is 13 meters and by my calculations net would be 11. The pipe through the dam wall is 100m and 300mm is diameter. The size of the turbine intake would allow 160l/s, 2.26m/s water velocity through the 300mm pipe which i used to get friction losses.
The turbine was built by Otago University here in NZ and ive been told that shaft RPM at 10m of head will be 880 at its most efficient speed. It is currently set up to run v belts.
All of the Power generated will need to go directly onto the grid but I have many meters on my bill so I have talked to the power company and the power created will cancel at 1-1 some of the other power I use.
Im still confused as to the possibility of over revving an induction motor that is of a larger rating than our maximum theoretical power available.
The motor I have is 22 Kilowatt, 400 volt, 1400 rpm induction motor. If maximum power is generated at 1442 RPM and I was to rev it up over this under no load then turn it on- would the torque created by the power generation not slow down the motor to below 1442 to an equilibrium point (still above synchronous speed) where the force created by the turbine would equal that by the generation of power by the motor (less losses due to belts, friction etc) eg 10kw.
I had looked into ram pumps but it would not be feasible.
Thank you very much for your time
Kind Regards
Tim