Whatever charge lead acid battery, charge process require energy. And according to Bedini there is difference when people charging with radiant circuit.
Here is the standard process of charging. Anyone has other version, feel free to post them.
Accu Oerlikon - battery power
The free reaction enthalpy is (at 25 °C): The delta of G=-372.2 kJ (standard)
The reversible voltage is H2SO4 concentration/activity dependent.
Typically a H2SO4 concentration of 28 % (3.4 mol/l) to 42 % (5.6 mol/l) with a density of 1.20 to 1.32 g/cm3 (20 °C) is present in a fully charged battery. This electrolyte freezes between -30 °C to -70 °C. Dilute solutions start freezing from -0.5 °C.
The standard reversible voltage (aH+; a HS04- = 1 mol/l) is:
U0 = - delta of G / n · F = 372.2 / 2 · 96500 = 1.928 Volt
The mass of reactants per unit reaction are:
207.2g Pb +239.2g PbO2+2g H+ + 194g HSO4-=642.4g PbSO4 +36 g H2O
The theoretical specific power of the lead/lead dioxide/sulfuric acid couple is:
(53.61 Ah)(1.928V / 0.6424 kg )= 160.9 Wh / kg
The practical energy density is however only in the range of 15 to 45 Wh/kg due to limitations in active mass utilizations and the weight of electrochemically inert accessories (container, grids etc.) as shown below.
Here is the standard process of charging. Anyone has other version, feel free to post them.
Accu Oerlikon - battery power
The free reaction enthalpy is (at 25 °C): The delta of G=-372.2 kJ (standard)
The reversible voltage is H2SO4 concentration/activity dependent.
Typically a H2SO4 concentration of 28 % (3.4 mol/l) to 42 % (5.6 mol/l) with a density of 1.20 to 1.32 g/cm3 (20 °C) is present in a fully charged battery. This electrolyte freezes between -30 °C to -70 °C. Dilute solutions start freezing from -0.5 °C.
The standard reversible voltage (aH+; a HS04- = 1 mol/l) is:
U0 = - delta of G / n · F = 372.2 / 2 · 96500 = 1.928 Volt
The mass of reactants per unit reaction are:
207.2g Pb +239.2g PbO2+2g H+ + 194g HSO4-=642.4g PbSO4 +36 g H2O
The theoretical specific power of the lead/lead dioxide/sulfuric acid couple is:
(53.61 Ah)(1.928V / 0.6424 kg )= 160.9 Wh / kg
The practical energy density is however only in the range of 15 to 45 Wh/kg due to limitations in active mass utilizations and the weight of electrochemically inert accessories (container, grids etc.) as shown below.