  • No Galvanic Isolation - High Risk? 120VDC Power Supply

    In an electronics forum I tried to open the topic of of taking a diode bridge and rectifying 120AC directly to 120VDC with capacitive smoothing for use as a power supply for a 60 plate electrolyser. My thoughts were that I needed the same number of volts on the AC side as the DC side, why involve a bulky, costly, and hot transformer, if unneccesary. My thread was immediately shut down due to the discussion of No Galvanic Isolation. The forum is very picky, anyone speaking of overunity, HHO, free energy, or anyone displaying any questionable circuitry with any home made components gets deleted.

    Is it really that dangerous? I see many others doing it and now I'm very curious. If it is truly that dangerous, I won't bother.

    Thanks
    Last edited by kcarring; 02-01-2011, 10:45 PM. Reason: typo
    ----------------------------------------------------
    Alberta is under attack... http://rethinkalberta.com/

    Has anyone seen my Bedini Ceiling Fan that pushes the warm air down, and charges batteries as an added bonus? Me neither. 'Bout time I made one!!!!! :P

  • #2
    rectifying 120VAC would give around 168VDC

    Comment


    • #3
      Originally posted by rave154 View Post
      rectifying 120VAC would give around 168VDC
      Ok. At a peak, correct? And your thoughts on the danger? I don't want to be doing something completely stupid and was pretty surprised to be "shut down" - the topic.. completely. I'm wondering if not employing galvanic isolation is as dangerous as implied.
      ----------------------------------------------------
      Alberta is under attack... http://rethinkalberta.com/

      Has anyone seen my Bedini Ceiling Fan that pushes the warm air down, and charges batteries as an added bonus? Me neither. 'Bout time I made one!!!!! :P

      Comment


      • #4
        Very Dangerous

        The problem with not using an isolation transformer is the very real danger of getting yourself or someone else electrocuted. One side of your normal AC 120 volt circuit is tied to ground. If you use a bridge directly off the 120 volt AC circuit then all of your circuit will be hot in reference to ground. Both your plus and minus side of the bridge is now above ground by about 70 volts or so. If you come into contact with any part of your circuit and ground at the same time you will now complete the circuit back to ground with a pulsating DC current going through your body. AC passing through your body causes the muscles to contract and may make it hard for you to turn loose. DC passing through your body burns a pathway causing potentially serious damage. Under the right circumstances either AC or DC can easily kill you. It only takes a few milliamperes to do. Always use an isolation transformer if working with Line powered AC devices.

        Be careful, Carroll
        Just because someone disagrees with you does NOT make them your enemy. We can disagree without attacking someone.

        Comment


        • #5
          Originally posted by citfta View Post
          The problem with not using an isolation transformer is the very real danger of getting yourself or someone else electrocuted. One side of your normal AC 120 volt circuit is tied to ground. If you use a bridge directly off the 120 volt AC circuit then all of your circuit will be hot in reference to ground. Both your plus and minus side of the bridge is now above ground by about 70 volts or so. If you come into contact with any part of your circuit and ground at the same time you will now complete the circuit back to ground with a pulsating DC current going through your body. AC passing through your body causes the muscles to contract and may make it hard for you to turn loose. DC passing through your body burns a pathway causing potentially serious damage. Under the right circumstances either AC or DC can easily kill you. It only takes a few milliamperes to do. Always use an isolation transformer if working with Line powered AC devices.

          Be careful, Carroll
          Thanks! No need to electrocute myself!
          ----------------------------------------------------
          Alberta is under attack... http://rethinkalberta.com/

          Has anyone seen my Bedini Ceiling Fan that pushes the warm air down, and charges batteries as an added bonus? Me neither. 'Bout time I made one!!!!! :P

          Comment


          • #6
            Originally posted by citfta View Post
            Always use an isolation transformer if working with Line powered AC devices. Be careful, Carroll
            Carroll,

            Do you think this might do the trick?
            YouTube - Isolation Transformer? What do you think?

            Thanks,
            Kyle
            ----------------------------------------------------
            Alberta is under attack... http://rethinkalberta.com/

            Has anyone seen my Bedini Ceiling Fan that pushes the warm air down, and charges batteries as an added bonus? Me neither. 'Bout time I made one!!!!! :P

            Comment


            • #7
              Look at this

              Kyle I think you would be better off with something like this one I found on Ebay.


              ISOLATION TRANSFORMER POWERTEC USA P/N 02-0010 PRI 120V - eBay (item 220700656500 end time Feb-20-11 14:28:23 PST)


              I didn't see anything in the video you showed that tells us what the inputs and outputs are. The link I have here is for a transformer that will handle 100 watts. Which means you will get about 160 volts after you rectify the AC to Dc and about 625 milliamps of current. If you tell me what kind of current and voltage you are looking for I'll tell you what you need to be looking for. Hope this helps.

              Carroll
              Just because someone disagrees with you does NOT make them your enemy. We can disagree without attacking someone.

              Comment


              • #8
                Originally posted by citfta View Post
                If you use a bridge directly off the 120 volt AC circuit
                then all of your circuit will be hot in reference to ground.
                Both your plus and minus side of the bridge is now
                above ground by about 70 volts or so.
                Actually, that is an incorrect statement.

                First,
                the most efficient usage of the available
                dual-polar voltage swings will always be
                four diodes in a full-wave bridge configuration.

                That is why all current electronic equipment I've seen
                uses it since people stopped using tubes as rectifiers...
                (Yeah, I'm that old)

                As one of the leads IS referenced to ground (Neutral),
                the minus side will ONLY be the diode's junction drop higher than that.

                Measure any of your transformer-less TV supplies...

                The other will have "Peaks" as high as noted,
                but the RMS value remains near the same.

                The "Peak" value does have merit
                to this conversation still though,
                because of rectification and smothing
                with a bank of electrlytic capacitors.

                The amount of cells MUST account
                for the TOTAL voltage sustained
                under the load presented by the cell.

                Factor for at least high 160's for voltage !



                The first plate on the negative side
                would be a diode's voltage drop from neutral.

                Each progressive plate away from it
                would then become more hazardous.



                Had the topic have been using L1 AND L2,
                meaning pole-1 and pole-2 of the electric service.

                Then your answer would have been completely correct.

                The mean-average voltage would be
                swung from both sides of neutral.

                In both cases, and in all equipment,
                having a safely grounded enclosure
                in case of failure a is paramount !

                even the L1+L2 scenario is no different
                than the 220-VAC clothes dryer you use...

                I hope this helps.
                Last edited by WeThePeople; 02-02-2011, 12:39 PM.

                Comment


                • #9
                  Sorry but I don't agree

                  To WeThePeople,

                  Sorry but I don't agree. Your conclusion would be correct if the hot side of the 120 AC never went below ground. But for half the cycle the hot side is negative in reference to the neutral side. Therefore the negative of the bridge will be about 60-65 volts negative in relation to the neutral. I may have misled you when I said all the circuit would be hot. I meant in reference to ground all the circuit will be live or will still bite if you touch it and ground at the same time. When the first transformerless TVs came out there were a lot of techs that blew up their scope leads when they tried to connect the ground lead of the probe to the negative of the circuits like they had always done before. Since the chassis of most scopes is connected to ground they created a short from the negative of the supply back to the neutral which was grounded. We learned real quick we had to start using an isolation transformer on our scope or cut off the ground pin of the power cord. I am also an old dog with many years of experience in making mistakes like that. Hope that explains it correctly.

                  Carroll
                  Just because someone disagrees with you does NOT make them your enemy. We can disagree without attacking someone.

                  Comment


                  • #10
                    Thanks

                    Thank-you to all those that have helped me understand better.

                    First off I have determined no matter what, the transformer I took a video of, up above is not what I am after, because it is not an isolation transformer, it is a step down transformer.

                    I need more watts.

                    The thing that gets me is I see Eagle Research machines utilizing the non-isolated method, and I wonder how on Earth that can be so I even mailed George and he simply stated "Yes, I definitely ground all the possible case enclosure points to the ground plug for safety".

                    But, once again, i still don't see the ultimate safety in that.

                    I'm left to think if the floor under you was wet and you actually touched one of the DC hot leads to actual electrolyser, you'd provide a path to ground across the mains.

                    There is a huge cost difference in providing this galvanic isolation (money wise).

                    If the electrolyser runs @ 120v (across 60 plates = 2v per plate) and for arguments sake, let's just imagine it drawing 8 amps, you have about 1000 watts. Or more, if you take that NaOH concentration up to or close to one mole solution. Then you might be drawing 10 amps.

                    So, we need about 800-1500 watts here!

                    And given that some prices go into the 4-500 range BUT....

                    maybe this would do:



                    Isolation Transformer
                    120v : 120v @ 12 amps

                    (TP) 500-144
                    Oneac isolation transformer. High isolation. Electrostatically shielded. Tap @ 10v, primary & secondary.

                    • 120v : 120v @ 12 amps
                    • Dimensions: 7-1/2" x 5-3/4" x 6-1/2"H
                    • Net Weight: 33 lbs

                    Isolation Transformers - 1 kva to 4 kva


                    Thanks for your input!
                    ----------------------------------------------------
                    Alberta is under attack... http://rethinkalberta.com/

                    Has anyone seen my Bedini Ceiling Fan that pushes the warm air down, and charges batteries as an added bonus? Me neither. 'Bout time I made one!!!!! :P

                    Comment


                    • #11
                      Dc- Dc isolation?

                      This, however appears to be DC-DC isolation? Could one bridge rectify to DC - THEN do isolation, leaving only a small encased portion of the project, at risk?
                      ----------------------------------------------------
                      Alberta is under attack... http://rethinkalberta.com/

                      Has anyone seen my Bedini Ceiling Fan that pushes the warm air down, and charges batteries as an added bonus? Me neither. 'Bout time I made one!!!!! :P

                      Comment


                      • #12
                        Maybe I should clarify what I am doing here.

                        I intend of using 120 vdc across a series of electrolyser anodes, so on one end you have - and many neutral plates later, you have +.

                        The exact number of neutral plates will be determined by the average potential available, given the power source SO when I revamp my electrolyser I need first determine what I have to work with.

                        Ultimately you will have between 1.75 and 2.3 v per cell. If smoothing were employed it would be ultimate to have that ripple vary from the above two figures, or close to.

                        I don't know much about voltage regulation, though I do understand capacitive smoothing.

                        The natural "pulse train" is a good thing, the variance.

                        If you like I can share with you the circuit I have, as purchased by Eagle Research, but I have to redo it, draw it myself as I probably shouldnt just scan the book and publish it.

                        Please view this video as it is nearly identical to what I am talking about.

                        This is what most guys are doing, and this is what I am concerned with, an identical situation... is this safe or not...?

                        YouTube - HHO 120V CELL DRIVER
                        ----------------------------------------------------
                        Alberta is under attack... http://rethinkalberta.com/

                        Has anyone seen my Bedini Ceiling Fan that pushes the warm air down, and charges batteries as an added bonus? Me neither. 'Bout time I made one!!!!! :P

                        Comment


                        • #13
                          Why not use a capacitive transformer instead if you are using voltage below mains? No inductors and very low loss.

                          Capacitive Battery Charger, incl. Capacitive Transformer | www.eagle-research.com

                          YouTube - DIY Capacitive Battery Charger

                          DIY Capacitive Battery Charger
                          Last edited by SilverToGold; 02-02-2011, 10:52 PM.

                          Comment


                          • #14
                            schematic

                            This video, goes over, in detail: the schematic to the previous video:

                            YouTube - HHO 120V SCHEMATIC
                            ----------------------------------------------------
                            Alberta is under attack... http://rethinkalberta.com/

                            Has anyone seen my Bedini Ceiling Fan that pushes the warm air down, and charges batteries as an added bonus? Me neither. 'Bout time I made one!!!!! :P

                            Comment


                            • #15
                              Originally posted by SilverToGold View Post
                              Why not use a capacitive transformer instead if you are using voltage below mains? No inductors and very low loss.

                              Capacitive Battery Charger, incl. Capacitive Transformer | www.eagle-research.com

                              YouTube - DIY Capacitive Battery Charger
                              Thanks. This may be what George does, and possibly I am not looking at all of this correctly. He states that he has avoided the use of a heavy, costly transformer. Which is what i want to do, if it can be done 100% safely.

                              Thanks Again.
                              ----------------------------------------------------